Note: Typo in the Title: AFDI s.b. AFGI; Pedatals = "Pedestals"; can't edit the titles...
This is on a 1972 43' DCFB, which I have owned since 1997. These are 120v Single Phase circuits on these vintage of boat. All circuits have ground wires, i.e. the outlets are triplex with a ground.
UPDATE to Arc-Flash Concerns:
NFPA 70E states any circuit 240 volt or less and supplied by a 125 kva or less transformer is exempt.
The premise is there is not enough current capability to maintain an arc flash.
Therefore 120 volt receptacles don't qualify to be rated, aka is rated HRC 0.
If any on here know otherwise, please indicate on this thread.
I will pull all the AFGI from here later... Thx...
Note of the You-Tube videos spells out the volts or kva
Apparently the vast majority of marinas where I have moored for the past 25+ years, did not have GFCI Pedestals. Now for the 2nd time in 10 years, I am tripping the breaker at the Dock Pedestal and have learned that it is GFCI, both 30amp, 50amp. I am tripping the 50amp, but not the 30amp (AC dedicated).
I am in the process of installing an "isolation" transformer on my 50amp input. Since the Pedestal only "sees" the Transformer, this should cease the 50amp Dock GFCI from tripping. The boat has several GFCI protected outlets, and I have never had an issue with them. I am told some boat owners have spent over $1,000 chasing Dock GFCI issues, to no avail!
FWIW, the transformer is an Acme 120v, 7.5Kva (50amp) shielded unit; weighs 105#'s. Ward Electric in FL installs a lot of these on boats.
What is occurring, is that many if not all marinas are now upgrading their electrical to GFCI at their pedestals. It is reported that marina managers are experiencing a large number of tripping of their GFCI equipped pedestals; this is true of the marina that has been servicing my boat. In addition, the Feds have lowered the trip points from 100ma to 30ma, i.e. much more sensitive. I have had several conversations recently with a marine engineer, and he says calls about tripping GFCI at the dock, are up 1,000% over the past year.
Also, in researching this issue, I have discovered that Arc-Flash can be a huge issue, and can occur on 120v circuits at 15 and 20amps. To prevent Arc-Flash, AFGI breakers are available. Since AFGI and GFCI sort of interfere with each other, there are combo AFGI/GFCI breakers, which eliminates the need for GFCI at the "wall".
Finally, since owning the boat, I had a 20amp Charger/Inverter installed, including a "Transfer" switch. Note that when the Inverter is engaged, its internal circuits only support 20amps, so that is a limiting factor; I will stop there.
So my questions are:
1) Do you have an Isolation Transformer? If you have an older boat (80's?), probably not.
2) Are you running into issues tripping GFCI pedetals in the past or more currently. They are new at many marinas now.
3) Do you have any AFGI breakers on your boat panel(s)? Many homes do not have AFGI breakers, so you would think boats would be so equipped even less.
Actually, I am a lot concerned about Arc-Flash, per the many You-Tube videos on the subject. Have an Arc-Flash on a boat, and "Goodbye" boat! I have seen nothing about GFCI or AFGI in the BoatUS (now Geico) publication.
End of my techie talk. My transformer is inbound to Grainger's next week. They had four in stock at this size (120v single phase, 7.5 Kva, 50am), so must be demand for them. $1,800, cheap at the price, if works!
Thanks...
This is on a 1972 43' DCFB, which I have owned since 1997. These are 120v Single Phase circuits on these vintage of boat. All circuits have ground wires, i.e. the outlets are triplex with a ground.
UPDATE to Arc-Flash Concerns:
NFPA 70E states any circuit 240 volt or less and supplied by a 125 kva or less transformer is exempt.
The premise is there is not enough current capability to maintain an arc flash.
Therefore 120 volt receptacles don't qualify to be rated, aka is rated HRC 0.
If any on here know otherwise, please indicate on this thread.
I will pull all the AFGI from here later... Thx...
Note of the You-Tube videos spells out the volts or kva
Apparently the vast majority of marinas where I have moored for the past 25+ years, did not have GFCI Pedestals. Now for the 2nd time in 10 years, I am tripping the breaker at the Dock Pedestal and have learned that it is GFCI, both 30amp, 50amp. I am tripping the 50amp, but not the 30amp (AC dedicated).
I am in the process of installing an "isolation" transformer on my 50amp input. Since the Pedestal only "sees" the Transformer, this should cease the 50amp Dock GFCI from tripping. The boat has several GFCI protected outlets, and I have never had an issue with them. I am told some boat owners have spent over $1,000 chasing Dock GFCI issues, to no avail!
FWIW, the transformer is an Acme 120v, 7.5Kva (50amp) shielded unit; weighs 105#'s. Ward Electric in FL installs a lot of these on boats.
What is occurring, is that many if not all marinas are now upgrading their electrical to GFCI at their pedestals. It is reported that marina managers are experiencing a large number of tripping of their GFCI equipped pedestals; this is true of the marina that has been servicing my boat. In addition, the Feds have lowered the trip points from 100ma to 30ma, i.e. much more sensitive. I have had several conversations recently with a marine engineer, and he says calls about tripping GFCI at the dock, are up 1,000% over the past year.
Also, in researching this issue, I have discovered that Arc-Flash can be a huge issue, and can occur on 120v circuits at 15 and 20amps. To prevent Arc-Flash, AFGI breakers are available. Since AFGI and GFCI sort of interfere with each other, there are combo AFGI/GFCI breakers, which eliminates the need for GFCI at the "wall".
Finally, since owning the boat, I had a 20amp Charger/Inverter installed, including a "Transfer" switch. Note that when the Inverter is engaged, its internal circuits only support 20amps, so that is a limiting factor; I will stop there.
So my questions are:
1) Do you have an Isolation Transformer? If you have an older boat (80's?), probably not.
2) Are you running into issues tripping GFCI pedetals in the past or more currently. They are new at many marinas now.
3) Do you have any AFGI breakers on your boat panel(s)? Many homes do not have AFGI breakers, so you would think boats would be so equipped even less.
Actually, I am a lot concerned about Arc-Flash, per the many You-Tube videos on the subject. Have an Arc-Flash on a boat, and "Goodbye" boat! I have seen nothing about GFCI or AFGI in the BoatUS (now Geico) publication.
End of my techie talk. My transformer is inbound to Grainger's next week. They had four in stock at this size (120v single phase, 7.5 Kva, 50am), so must be demand for them. $1,800, cheap at the price, if works!
Thanks...